Electrical grounding systems divert potentially dangerous electrical currents by providing a path between a building’s service boxGrounding Rod and the earth. Lightning and static electricity are the most common sources of dangerous or damaging charges that can be dissipated through a grounding system. Grounding electrodes are connected to the building’s electrical system through grounding electrode conductors, also known as ground wires. A number of different metal alloys can function as grounding electrodes, the most common of which are the focus of this article.
Requirements for electrodes and ground wires:
- Aluminum has a tendency to corrode and should not be used in ground wires unless they are insulated. Moisture and mineral salts from masonry are common causes of corrosion to uninsulated aluminum. It is also a poorer conductor than copper. Aluminum wires in grounding systems are not permitted in Canada.
- Since grounding electrodes are not insulated, they can never be made of aluminum.
- If more than one electrode is present, they must be connected to each other with a bonding jumper.
Common Types of Grounding Electrodes Grounding Rods
The most common form of grounding electrode is a metal rod that is hammered into the ground so that its entire length is submerged. InterNACHI recommends that the rod be inserted vertically and in one piece, but this is not always possible in rocky areas. If the rod is hammered into sub-surface rocks it might become scratched and lose its cladding. Rust can accumulate on exposed iron or steel and degrade the conductive capacity of the rod. Unfortunately, this rust will rarely be visible to an inspector.
Electricians have been known to cut the rod when they have difficulty inserting its entire length beneath the ground. This practice violates code and can be a safety hazard. Inspectors should look for the following signs that indicate that a grounding rod has been shortened:
- Rust at the rod’s top. Grounding rods have a corrosion-resistant coating but are usually made of steel or iron and are vulnerable to rusting at any location that the rod is cut.
- Most rods have an etched label on their top. If this label is missing it is likely that the rod has been cut.
Inspectors should bear in mind that utility companies sometimes allow ground rods to be shortened. A qualified electrician can test whether a shortened rod is an adequate grounding electrode.
If accessible, inspectors should check the condition of the clamp that connects the grounding rod to the ground wire. Clamps should be made of bronze or copper and be tightly fastened. Requirements for rod length, thickness, and protective coating are addressed in the 2006 International Residential Code (IRC) as follows:
Rod and pipe electrodes not less than 8 feet (2438 mm) in length and consisting of the following materials shall be considered as a grounding electrode:
- Electrodes of pipe or conduit shall be not smaller than trade size ¾ (metric designator 21) and, where of iron or steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection.
- Electrodes of rods of iron or steel shall be at least 5/8 inch (15.9 mm) in diameter. Stainless steel rods less than 5/8 inch (15.9mm) in diameter, nonferrous rods or their equivalent shall be listed and shall be not less than 1⁄2 inch (12.7mm) in diameter.
Notes
- Although the 2006 IRC does not mention whether the rod may be driven at an angle, the 1998 California Electrical Code allows for a maximum oblique angle of 45 degrees from the vertical.
- An electrician can install two grounding rods if necessary. They should be at least 6 feet apart from one another.
- In Canada, grounding rods should be 10 feet long and two are required.
http://www.nachi.org/grounding-electrodes.htm